Well, that’s a 110v ac control system
Single phase motor
And a high pressure shutdown
Welcome to ScubaBoard, the world's largest scuba diving community. Registration is not required to read the forums, but we encourage you to join. Joining has its benefits and enables you to participate in the discussions.
Benefits of registering include
Well, that’s a 110v ac control system
Either the overloads are too small or the motor is bad. A megohm meter will tell you.Suspected faulty 5hp 1ph 230 v motor, apparently it trips the thermal breaker after a few minutes. Will be doing a little more research
I have not. This weekend i will shoot for a test. Pump rolls easily by hand though if that makes it any different.Either the overloads are too small or the motor is bad. A megohm meter will tell you.
Or the pump is dragging. Have you heard it run yet?
This is probably the edge of what's done.5HP or 3.7kW on a single phase is pretty impressive. Draws about 28 amps.
Is that done a lot in the US? Here, anything above 3kW is 3-fase.
That kind of draw should be on at least a 40 amp, 240 circuit. Get an amp meter and monitor thr running current draw. If it is basically around the motor rating, watch for a while to see if it varies much.
I'm in Ciincinati or I would come down and check it for you.